I'm in the US, and I've done extensive house wiring here, but I know
nothing about what is acceptable or even legal in other countries.

In the US, we run 120V for regular wall outlets.  The regular receptacles
are rated at 15A.  The wiring needs to be rated for at least 15A, and the
fuse/breaker can be rated no higher than the rating of the smallest wiring
conductor between the breaker and outlets.  This is typically 14 gauge
(with a 15A breaker) or 12 Gauge (with a 20A) breaker.  That breaker
typically supplies *multiple* 15A receptacles, with the idea that they
aren't going to all draw their rated maximum at the same time (if ever).
And if they do, the breaker trips or the fuse blows to protect the wiring.

So my question is, do other countries allow wiring with oversized
breakers?  Why didn't Cheater's fuse/breaker save the day?  I would expect
breakers in 240V countries to be even smaller thanks to Mr. Ohm.

On Fri, Jan 14, 2022 at 8:13 AM Mike Bryant <mbryant at futurehorizons.com>
wrote:

> 26 Amps is also marginal for the house wiring in many European countries.
>   Europeans never did understand the advantages of UK ring mains which are
> of course compulsory here in most situations :-)
>
> -----Original Message-----
> From: Synth-diy [mailto:synth-diy-bounces at synth-diy.org] On Behalf Of
> Gordonjcp
> Sent: 14 January 2022 13:55
> To: synth-diy at synth-diy.org
> Subject: Re: [sdiy] OT: Mains Safety PSA
>
> On Fri, Jan 14, 2022 at 12:33:06PM +0100, cheater cheater via Synth-diy
> wrote:
> > So as recent experience shows, 18 - 26 amps max continuous load for
> > months was a tad optimistic for this unknown brand Schuko wall socket,
>
> 18A is somewhat and 26A is grossly out of spec for Schuko.
>
> If you're going to pull that kind of power you need to look into getting a
> dedicated circuit and IEC60309 sockets fitted.  We use the 16A version for
> our "small" cabinets (where they mostly just power a single 24V rackmount
> PSU, with extra "UK plug" BS1363 sockets for plugging in test equipment.
> For our server cabs we use the 32A version.
>
> You might want to use the 32A version, too.
>
> --
> Gordonjcp
>
> _______________________________________________
> Synth-diy mailing list
> Synth-diy at synth-diy.org
> http://synth-diy.org/mailman/listinfo/synth-diy
> Selling or trading? Use marketplace at synth-diy.org
>
>
> _______________________________________________
> Synth-diy mailing list
> Synth-diy at synth-diy.org
> http://synth-diy.org/mailman/listinfo/synth-diy
> Selling or trading? Use marketplace at synth-diy.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://synth-diy.org/pipermail/synth-diy/attachments/20220114/73122b4e/attachment.htm>


More information about the Synth-diy mailing list