[sdiy] measuring dc current max/draw of psu with a scope or multimeter??
Chris Juried
cjuried at yahoo.com
Thu Dec 10 18:09:53 CET 2015
I use an isolation transformer in line with my scope's mains power, as Ritchie suggested. They are a cost effective protection measure which I highly recommend, for the safety of you and your equipment.
Sent from Yahoo Mail on Android
On Thu, Dec 10, 2015 at 11:21 AM, Doug Forbes<dougforbes at dslextreme.com> wrote: How about just get a digital multimeter from Harbor Freight for $6 or for free when they have a coupon ?
http://www.harborfreight.com/7-function-digital-multimeter-90899.html
On 12/10/2015 8:07 AM, Richie Burnett wrote:
You need to be careful with grounding if you use a current sensing resistor and an oscilloscope to measure current draw from a power supply. For instance, if both the power supply and oscilloscope are grounded to the mains supply earth, and you put the current-shunt resistor in the V+ feed (high-side sensing) to measure the current there, then you can't just connect one oscilloscope probe across the resistor to measure the voltage drop. Connecting the scope's ground clip will short the V+ supply to ground through the scope, possibly damaging either the scope or power supply!
The solutions are:
1. Power the scope from an isolation transformer.
2. Use a battery powered "Scopemeter" that isn't earthed.
3. Run the power supply from an isolation transformer with it's earth floated.
4. Use a Class-II power supply that isn't earthed.
5. Use two scope probes to measure the voltage drop in (Y1-Y2) differential measurement mode.
6. Move the sense resistor into the 0v line of the power supply and connect the scope probe ground lead to the PSU ground side.
Note, method 6 is only acceptable if the current flowing in the 0v line is the same as the current you wanted to measure. This is fine for something like a single output +12V power supply, but measuring the ground current won't work for a multi-output +5V/-12V/+12V power supply where all of the wires will likely carry different currents.
Hope this helps,
-Richie,
-----Original Message----- From: Vladimir Pantelic
Sent: Thursday, December 10, 2015 2:58 PM
To: synth-diy at dropmix.xs4all.nl
Subject: Re: [sdiy] measuring dc current max/draw of psu with a scope or multimeter??
On 10.12.2015 15:48, Dan Snazelle wrote:
im trying to figure out if this is possible witn regular tools
i know i could buy a dc ammeter but those are expensive
ive also read about current probes but some of these seem to saturate at 500ma dc
so
i figured there must be a way to test current with a resistor and voltage
any ideas??
if you put a 0.1 Ohm resistor in-line with the PSU, then a current of 1A
will give you a voltage of 0.1V that you can read/measure with the
scope. if the voltage drop is too high, you can go to a lower resistance
as long as you can reliably measure the voltage. make sure the resistor
has a tight tolerance e.g. use a precision shunt.
_______________________________________________
Synth-diy mailing list
Synth-diy at dropmix.xs4all.nl
http://dropmix.xs4all.nl/mailman/listinfo/synth-diy
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2016.0.7294 / Virus Database: 4483/11152 - Release Date: 12/10/15
_______________________________________________
Synth-diy mailing list
Synth-diy at dropmix.xs4all.nl
http://dropmix.xs4all.nl/mailman/listinfo/synth-diy
_______________________________________________
Synth-diy mailing list
Synth-diy at dropmix.xs4all.nl
http://dropmix.xs4all.nl/mailman/listinfo/synth-diy
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://synth-diy.org/pipermail/synth-diy/attachments/20151210/401b7467/attachment.htm>
More information about the Synth-diy
mailing list