On Dienstag 03 Juni 2008, James Dunn wrote:
> The thing is, I'm in the UK and would like to connect the two
> primaries in series but I can't identify the phase of each winding.
Chose any numbering and connect 2&3. Leave 4 open and apply 110V
between 1&2. If you can measure about 220V between 1&4, then things
are correct, otherwise switch 3&4 and try again.
1o--- ||
.)||
)||
)||
2o-*- ||
| ||
3o-*- ||
.)||
)||
)||
4o--- ||
Achim.
--