UPS battery advice
Doug Tymofichuk
dougt at cancerboard.ab.ca
Tue Apr 11 16:24:48 CEST 2000
On Mon, 10 Apr 2000 11:58:55 -0700 "nss at hevanet.com"
<nss at hevanet.com> wrote:
> A few years back I bought a UPS/filter that will run all my
> gear and computer for 20 min or so, and I'll say I'll never
> plug my stuff into the wall without somthing similar again!
If your UPS is 2 years old or more: CHANGE THE BATTERIES!!
Most computer UPS units use sealed lead-acid batteries for
back-up power. Most UPS units are run with the power on,
charging the internal batteries, 24 hours a day, 365 days
per year. After a couple of years you will find their
capacity has been SEVERELY diminished due to overcharging,
so when the power goes out, so does the UPS. You should
also test that the UPS can power your equipment for at
least 10 minutes on a regular basis (monthly). People tend
to forget that there are batteries inside these units,
until they no longer work.
----------------------
Doug Tymofichuk
dougt at cancerboard.ab.ca